check out the new remote control Jockey Wheel SmartBar Canegrowers rearview170 Cobb Grill Skid Row Recovery Gear Caravan Industry Association of Australia
Members Login
Username 
 
Password 
    Remember Me  
Post Info TOPIC: wiring in new batteries


Senior Member

Status: Offline
Posts: 122
Date:
wiring in new batteries


hi, getting two new batteries but the battery posts are further apart than previous battery, so wires won't reach, also will be running them in parallel which would make the - even longer.  What is the recommended fix for this? the exisiting battery has about 3-4 wires connected to each post. Is their some sort of junction box i could put the end in and then connect one longer wire to new battery. One of = and -

 

I dont want to replace all existing wires.

 

cheers in advance

 

peter

 

 

 



__________________


Guru

Status: Offline
Posts: 4375
Date:

Whatever else you do, there must be a fuse close to the battery that protects the cables in case of a short circuit.
If you don't have this it may help to "fill the gap" too.
Cheers,
Peter

__________________

OKA196, 4x4 'C' Class, DIY, self contained motorhome. 960W of solar, 400Ah of AGMs, 310L water, 280L fuel. https://www.oka4wd.com/forum/members-vehicles-public/569-oka196-xt-motorhome
 

 



Senior Member

Status: Offline
Posts: 122
Date:

ta.....



__________________


Guru

Status: Offline
Posts: 1315
Date:

If you wire all the loads and charging to one battery and just run the cables to the other battery in parallel, you will kill the battery carrying the loads early in its cycle life and it will then kill the other battery because it will place a constant drain on it yet absorb all the charging current.
Ideal fix, all the positive loads and charging cables to one point and the same with the negative cables, then run equal length positive cables (of a decent conductor size) to each battery positive terminal, then the same with the negative cable. All four cable don't need to be the same length, just the two positives must be the same and the two negatives must be the same.
The half *rsed way to do it, put the load/charging negatives on one battery and the positives on the other battery while linking the two batteries in parallel, it will help share the load, but not near as well as equal length cables to a common distribution point will.

T1 Terry

__________________

You can lead a head to knowledge but you can't make it think. One day I'll know it all, but till then, I'll keep learning.

Any links to any sites or products is not an endorsement by me or do I gain any financial reward for such links 



Guru

Status: Offline
Posts: 1931
Date:

stoney123 wrote:

hi, getting two new batteries but the battery posts are further apart than previous battery, so wires won't reach, also will be running them in parallel which would make the - even longer.  What is the recommended fix for this? the exisiting battery has about 3-4 wires connected to each post. Is their some sort of junction box i could put the end in and then connect one longer wire to new battery. One of = and -

I dont want to replace all existing wires.  cheers in advance,  peter

--------------------------------------------------------------------------------------------------------------------------------------------------------------------------- 

Hi Peter smile

You can get connection bars with a box to cover them like this as used in house meter boxes.   https://www.ebay.com.au/itm/Tesla-7-Hole-Active-Link-Red-Cover-Numbered-Terminal-100A-500V-Max-Cable-25mm2/322484927613?hash=item4b15997c7d:g:TXYAAOSwGUBaC4op&frcectupt=true

If you go to any electrical supply shop they will have them too, in black and red cover boxes.  The biggest holes would be OK for a battery cable. So you could make up some cables to go to the two batteries + and - terminals, and make them the same lengths to each battery. Or buy some cables with an eye terminal at an auto place. Then mount the terminals and boxes securely where the cables all fit well.

Jaahn                    



-- Edited by Jaahn on Monday 30th of September 2019 02:41:15 PM



-- Edited by Jaahn on Monday 30th of September 2019 03:03:05 PM

__________________


Senior Member

Status: Offline
Posts: 159
Date:

Hi Terry,

While I agree with your ideal parallel wiring  configuration for more than two batteries in parallel, I am not sure I would agree that your half  *rsed approach  for two parallel batteries is not as good or even better, assuming  equal length inter battery connecting cables.

The reason I think this is that if all positives and negatives  are connected to their respective common points and the connected to each battery by equal  length (resistance) cables as you suggested, then each battery will effectively have Ra plus Rb in series with the battery (where Ra = cable resistance of cable connected to positive common and Rb = resistance of cables connected to negative common)

Alternately taking the half *rsed approach, the positives are connected directly to one battery with a cable of resistance R connecting it to the second battery. Similarly the negatives are connected directly to the second battery which is connected to the "first"  battery with a similar cable of resistance R.

Comparing the two arrangements ;

Ideal approach : cable resistance  in series with each battery = Ra+Rb

Half *rsed approach:  cable resistance in series with each battery = R

If interconnecting cable resistance R < Ra+Rb then surely the half *rsed is better in this situation.

If connecting more than two batteries in parallel then the half *rsed approach is not the best.

You have suggested the half *rsed approach is not as good as the ideal appoach for connecting two batteries in parallel, but I don't see why, and I would really appreciate your advice and your mathematical analysis if my analysis is incorrect.

Ken

 



-- Edited by kgarnett on Wednesday 2nd of October 2019 05:53:36 PM



-- Edited by kgarnett on Wednesday 2nd of October 2019 05:54:33 PM



-- Edited by kgarnett on Wednesday 2nd of October 2019 06:03:55 PM

__________________


Guru

Status: Offline
Posts: 1931
Date:

Hi Ken smile

I would be happy to use this method and do not consider it "half *rsed". Indeed it is shown on lots of sites for boating and caravanning for wiring dual batteries. Easy to do and not much harder than the 'wrong way' as is often the case really.

Jaahn

 

Connecting Two Batteries in Parallel

from;     https://caravanchronicles.com/guides/how-to-connect-two-batteries-in-parallel/



__________________


Guru

Status: Offline
Posts: 4375
Date:

For low and moderate loads with 2 batteries, I agree.
For high loads from more than 2 batteries, I use the "star" method which involves taking all the positives and negatives to common points with equal length cables and distributing from there.
Cheers,
Peter

__________________

OKA196, 4x4 'C' Class, DIY, self contained motorhome. 960W of solar, 400Ah of AGMs, 310L water, 280L fuel. https://www.oka4wd.com/forum/members-vehicles-public/569-oka196-xt-motorhome
 

 



Guru

Status: Offline
Posts: 7314
Date:

If you are charging at a high current it would be better to get the wiring installed the best way you can.

You are investigating a lot of money in batteries so personally I would invest a bit extra get sort the wiring problem sorted out from the start.



__________________

Procrastination, mankind's greatest labour saving device!

50L custom fuel rack 6x20W 100/20mppt 4x26Ah gel 28L super insulated fridge TPMS 3 ARB compressors heatsink fan cooled 4L tank aftercooler Air/water OCD cleaning 4 stage car acoustic insulation.



Guru

Status: Offline
Posts: 1315
Date:

The part you have missed from the equation is the internal resistance of each battery. In the half *rsed approach, the battery with the least resistance will still do all the work until its voltage drops lower than the other battery, then the load will shuffle between the 2 batteries. The reverse happens when recharging but the issue gets worse because the battery to reach the end of boost voltage first, the one with the highest resistance, calls the shots and the charging voltage drop back to absorption and float voltages. The low to moderate load on batteries connect in less than the ideal configuration for multiple similar voltage batteries as even harder on the battery with the lowest resistance, basic maths will show why that is the case.

If each battery had zero internal resistance then what you say would be correct because only the cable resistance comes into the equation. No battery has zero internal resistance, not even a lithium battery, each cell has resistance and cells connected in series means this resistance is added together to create the total internal resistance of the battery.
Alternatively, if the cells are connected in parallel the cell resistance is the average of all the cells within that parallel group. Connect this group with another equal capacity group and the resistance is group 1 + group 2. Build 4 of these together in the case of a 12v lithium battery, you have resistance 1 + resistance 2 + resistance 3 + resistance 4 = total battery resistance. This resistance will alter as the state of charge alters and the load/charging current alters, but it is only one battery and the current must pass all the cells in the battery. The resistance balances out across all the cells in parallel resulting in all the cells maintaining a much closer state of charge to the cell beside it in the parallel group and all the groups in series means the same current has flowed out of or into each group.
This is the ideal way to build a battery, every step away from this ideal level adds a degree of imbalance between each cell that makes up the total battery and adds to the likelihood of a cell failure.
So what I posted as the ideal method was to get the best possible result for multiple similar voltage batteries connected in parallel, the ideal battery is built to the required capacity at cell level and the required voltage by connecting those cells in series.

T1 Terry

__________________

You can lead a head to knowledge but you can't make it think. One day I'll know it all, but till then, I'll keep learning.

Any links to any sites or products is not an endorsement by me or do I gain any financial reward for such links 



Senior Member

Status: Offline
Posts: 226
Date:

As T1 Terry has said many times that you do not connect lithium batteries together, so how lithium batteries are made is not relevant.
The controller monitors voltage and current into the circuit.
The circuit loop is the controller, the cables and the batteries.
Therefore we treat the controller as a voltage source, the cables as resistances and the batteries
as voltage sources with their internal resistances in parallel.
Kirchhoff's 2nd law states:
"The directed sum of the potential differences (voltages) around any closed loop is zero."
This means that if the cable resistances are equal then the battery voltages must be equal.
If they are not equal when first connected together the battery with the highest voltage will discharge through the other battery thereby charging it until both have the same voltage.
The internal resistances only effect the rate of charge and discharge.
Any tendency for one battery to supply more than the other, drops its output voltage due to its internal resistance and then the other battery supplies more of the load.
Think of two interconnected water tanks with filling tap and a outlet tap.
As long as the interconnection capacity exceeds the supply or drain rate it is self balancing.
The same applies to batteries.

__________________


Guru

Status: Offline
Posts: 1315
Date:

jegog wrote:

As T1 Terry has said many times that you do not connect lithium batteries together, so how lithium batteries are made is not relevant.
The controller monitors voltage and current into the circuit.
The circuit loop is the controller, the cables and the batteries.
Therefore we treat the controller as a voltage source, the cables as resistances and the batteries
as voltage sources with their internal resistances in parallel.
Kirchhoff's 2nd law states:
"The directed sum of the potential differences (voltages) around any closed loop is zero."
This means that if the cable resistances are equal then the battery voltages must be equal.
If they are not equal when first connected together the battery with the highest voltage will discharge through the other battery thereby charging it until both have the same voltage.
The internal resistances only effect the rate of charge and discharge.
Any tendency for one battery to supply more than the other, drops its output voltage due to its internal resistance and then the other battery supplies more of the load.
Think of two interconnected water tanks with filling tap and a outlet tap.
As long as the interconnection capacity exceeds the supply or drain rate it is self balancing.
The same applies to batteries.


You didn't add in the internal resistance of each cell in each battery adding together, nor the increased resistance between the first battery in the parallel string and the last battery in the parallel string. If the internal across a battery requires a voltage higher than the rested voltage to allow a current flow and the inverse when discharging, the voltage being similar is not an indication the capacity is similar. This is where the water analogy falls over.

As an example for those interested in testing out the theory, find a lead acid battery with a resting voltage of 12.7v, not fully charged but close to it. With a clamp meter to measure current flow and a volt meter on the charging source and another on the battery, dial up 12.7v at the charging source. At this point the water analogy will hold up as there should be zero current flow. Now dial up the charging source to 12.8v. The water analogy says there should be current flow between the supply and the tank with the lower capacity, a very small current flow will be seen on the clamp meter for a very brief period, then it will stop because both the battery voltage and supply voltage is the same. Now disconnect the battery, does the voltage remain at 12.8v? If the supply had topped the battery up till its internal storage was now enough to hold 12.8v now rather than the settled 12.7v.

With the water analogy, the tank would now have increased its capacity to equal the supply capacity, did the battery do the same thing?

For those that are interested in taking this further, keep increasing the supply voltage until you see a constant current flow meaning the capacity of the battery is actually increasing, not just the terminal voltage. How high was the source voltage above the 12.7v rested battery voltage before current actually started to flow constantly indicating the battery capacity was being increased?

Kirchhoff's 2nd law applies to circuits where the source voltage is established, does it allow for a leaking capacitor within with a zenor diode in the circuit?

A hint to just how much voltage differential is required to over come the internal resistance comes from the battery manufactures charging graphs and the quality charger maintenance routine voltages. If 12.8v (rested voltage of a fully charged lead acid battery) was enough to keep a 12v battery fully charged, why is the maintenance voltage set to 13.6v?   

T1 Terry



__________________

You can lead a head to knowledge but you can't make it think. One day I'll know it all, but till then, I'll keep learning.

Any links to any sites or products is not an endorsement by me or do I gain any financial reward for such links 



Guru

Status: Offline
Posts: 997
Date:

Pretty obvious Stoney123 wanted a simple answer, (as give by Jaahn) Stoney gave up in October. Turning out to be the longest battery install in history.

Amen.



__________________

Chris & Sharyn.

Mitchells Island. NSW.

2016 D-Max, 2012 Jayco Sterling, 1 dog, wife n me.



Guru

Status: Offline
Posts: 1315
Date:

The Travelling Dillberries wrote:

Pretty obvious Stoney123 wanted a simple answer, (as give by Jaahn) Stoney gave up in October. Turning out to be the longest battery install in history.

Amen.


The great thing about a forum compared to a one on one question and answer, a lot of knowledge is shared across a lot of people and for a lot longer period if the search function is used.

 

T1 Terry 



__________________

You can lead a head to knowledge but you can't make it think. One day I'll know it all, but till then, I'll keep learning.

Any links to any sites or products is not an endorsement by me or do I gain any financial reward for such links 



Guru

Status: Offline
Posts: 7640
Date:

Ahhh save all arguments . Start the generator !! Ahahaha . Big stirring spoon !! Lol .. I have 35mm sq various load connections ..

__________________
Whats out there


Veteran Member

Status: Offline
Posts: 50
Date:

The Travelling Dillberries wrote:

Pretty obvious Stoney123 wanted a simple answer, (as give by Jaahn) Stoney gave up in October. Turning out to be the longest battery install in history.

Amen.


 Pretty obvious there is no simple answer, but plenty of simple mistakes to make.  Personally I've learnt a hell of a lot from these threads.



__________________

Cheers

 

Gazza

Page 1 of 1  sorted by
 
Quick Reply

Please log in to post quick replies.

Tweet this page Post to Digg Post to Del.icio.us
Purchase Grey Nomad bumper stickers Read our daily column, the Nomad News The Grey Nomad's Guidebook