Hi guys. Wondering if someone can help me out. I have a 60lt adventure kings fridge. Seems to be exactly the same as a weaco cf60. It has the secop bd35f compressor. The fridge compressor and fan are running but the fridge isn't cooling. The pipe that comes out of the evaporator(I think, the radiator looking thing) gets ice on it and it runs into the fridge compartment. The thermistor seems to be working. I was getting about 15k ohm at about 15 degrees c. The compressor will run wether it's in emergency or if I connect the c and t together on the compressor board or if it'd normal mode.i am thinking it's low on gas or something although I can't see any leaks or oil where there could be a leak
Any help is much appreciated.
Mike Harding said
08:21 AM Oct 7, 2022
Sorry to say but it sounds very much as though it's lost its gas.
Whenarewethere said
08:46 AM Oct 7, 2022
Agree.
If you pull the fridge apart a lot of the soldered joints are pretty second rate work. My guess it is pretty much the same regardless of the manufacturer of the fridge.
Rohendo said
03:45 PM Oct 14, 2022
Thanks for the help. I'll pull it apart and have a look. It doesn't work now anyway.